Home > categories > Minerals & Metallurgy > Raw Materials For Refractory > How long is the fire endurance of fire resistant rolling shutter door?
Question:

How long is the fire endurance of fire resistant rolling shutter door?

How long is the fire endurance of fire resistant rolling shutter door?

Answer:

According to the requirements of Building Regulations 7.5.1 article,the fire endurance of class A fire resistant rolling shutter door should be no less than three hours.
According to the new national standards GB_12955-2008 for fire doors from January 1, 2009, fire doors are classified acoording to thermal insulation fireproof door(A),part heat insulation fireproof door(B) and non thermal insulation fireproof door(C), rather than thermal insulation fireproof door. At the same time, the original fire endurances of class A, B and C fire doors are adjusted to 1.5h, 1.0h and 0.5h respectively. So, GB is 1.5h
According to fire endurance, fire doors can be divided into Class A, Class B and Class C fire doors, whose fire resistance should be no less than 1.20h, 0.90h and 0.60h respectively. You can use fire resisting shutters to seperate fire?compartments in places where it is difficult to set firewalls. When using the fire resisting shutter with unexposed surface temperature rise as fire endurance conditions, its fire endurance should be no less than 3h. But when using the fire resisting shutter without unexposed surface temperature rise as fire endurance conditions, you should set independent protection of closed automatic water spray system at two sides of the shutter, and the duration of water spraying should be no less than 3.0h. I hope it's useful.

Share to: