Question:

How much cable does the construction elevator 44KVA need?

How much cable does the construction elevator 44KVA need?

Answer:

44KW three phase power: 79A, BV5X16
44 kva? What elevator, convert the high piezoelectric 44kva to power 35.2 KW, current 80A16 square cable
44 kva should choose 16 + 2 * 3 * 6 square cable, 16 of the 30 ℃ safe carrying capacity is 78 a cable Current I = P/U / 1.732 = 44000/380/1.732 is approximately 67A The construction elevator will not only carry the engineering materials but also the higher frequency, the load calculation will be calculated according to the continuous working system. The cable should be used for the YGTZ special cable.