Question:

Please consult some small questions about the connection between MITSUBISHI PLC and hand wheel encoder

My TYPE encoder is E FUTURE LIFE, Taiwan TECHOLOGY MANUAL PULSE GENERATOR 100PPR production, there are 5 lines, namely: 5V, 0V, A, B, /A, /B PLC FX1S, I know that the high speed input X0-X7 and high-speed counter of C235-C255. The question now is how to signal encoding device received PLC? I tried a connection, or X has no signal, or that X has been turned on, thank you very angry!

Answer:

Upstairs only stay in writing stage, in fact, 5V differential encoder to connect PLC, 24V, TTL input, not through the transformation, there is a way.Sorry, I haven't used MITSUBISHI PLC.But I have received an OMRON PLC.
I am sorry to tell you that the encoder is connected to your PLC is not appropriate, because the encoder is 5V differential output, while PLC can only meet the load of 12v-24v, if you want to use or re select the encoder to 24V NPN open collector output, it is easy to handle, either the converter will 5V signal to 24V.
The MITSUBISHI PLC is connected to the handwheel encoderSearch data library PLC application case information, free search, you can go up to see
The simplest way is to have a series divider resistor, or with an optocoupler.