Home > categories > Electrical Equipment & Supplies > Electrical Wires > the law of calculating the electrical wire size, plug socket in amperes and outlet socket in amperes?
Question:

the law of calculating the electrical wire size, plug socket in amperes and outlet socket in amperes?

fore an electric stove of 3000 watts, taking into consideration that the voltage in my country is 220volts

Answer:

Use Ohms Law, compute the (Current + Future Load + allowance), 10% would be enough if it is a direct cable to your stove, but if you want to add more load, then you have to consider them in the calculation, and when you consider the size of wire look at the manufacturers table for the correct size. Below is the formula: PPower in Watts ICurrent in Amps EVolts RResistance in Ohms EI*R PI*E IP/E Always put a separate circuit breaker when your add something this big to your line.
The law is the Voltage.nananaana.their it is
50 amps
Follow the link below and go to the theory page. It has all the formulas necessary for you to find what you're looking for. Good luck.
Most people would not calculate the wire size, but would calculate the current value and chose a wire size from a table. Your country's electrical code will tell you the wire size needed for the current necessary to supply the stove. This will be around 13.5 amperes. In the US this would require #14 conductors.

Share to: