Home > categories > Machinery & Equipment > Building Hoist > What is the need for the sc200/200 construction elevator cable?
Question:

What is the need for the sc200/200 construction elevator cable?

What is the need for the sc200/200 construction elevator cable?

Answer:

General is 3 times 16 + 2 * 6, want to know can seek professional construction lift machine cable market manufacturer ask
The company now USES 3X25 + 2x10 cables
The sc200/200 construction elevator cable line should not be below 120 square. Man's ladder 33KW, 5 * 33 = 165KW The tower is 45KW one, 2 * 45 = 90KW The pressure slag welder is estimated to be 25KW Touch welder 1OKW, 5 * 10 = 50KW Other facilities such as mixer, temporary illumination etc. 30KW Total power: 165 + 90 + 25 + 50 + 30 = 365KW One square cable is 5 minus 7A, 380V is 1KW is equal to 2A. That's 730A 730A divided by 5-7 calculates that the cable line should not be less than 120 square.

Share to: