Question:

22KW pump motor direct start circuit breaker and contactor size? Concrete calculation method

22KW pump motor direct start circuit breaker and contactor size? Concrete calculation method

Answer:

It's better not to start directly. It's a great test for your motor and contactor. Do a star three start, conditional on doing a star three plus autotransformer start, reducing the starting current. Reduce future maintenance costs. Since do not think about every day to do pump repair.
Strictly speaking, eleven kilowatts or more is not allowed to start directly
22KW the water pump motor is 380V. 22KW rated current is about 44A, 10 square copper wire is enough, the motor will often start off ah, if it is not available for DZ108-63 50A, CJX2-50 50A contactor is 380V.Pump motor (pump motor) according to the structure classification, should be divided into horizontal motor and vertical motor. Because of the work characteristics of pump starting torque is relatively small, the starting frequency is relatively small, relatively long time continuous operation and other characteristics, so the majority of pump motor asynchronous motor cage rotor or synchronous motor.The pump motor should be selected according to the selection of shaft power; motor shaft power power is greater than one level; for example: axle power is 15KW, select the motor should be: 18.5KW for motor with very few, according to the actual working conditions. 2 pole motor is generally used in the head of micro height, flow is not large (calculation is more complicated). Large flow, small lift occasions can choose 4 pole motor. Super large flow, lower head select 4 or 6 pole motor, when choose six pole motor, power can be reduced according to the shaft power of a grade.

Share to: