That is, some parameters of the inverter, such as torque, current, frequency, etc., are displayed on the Kingview software interface, but not through the PLC. The idea that the MODBUS protocol between SIEMENS and 200PLC has never been successful before, so that's the idea of the ABB. If it can be achieved,Is it necessary to write the script program on the Kingview, and what problems should I pay attention to when using the MODBUS protocol in Kingview software?The problem is a little bit more, I hope the experts teach me this rookie! Thank you
As long as there are 485 communications can be, the frequency converter manual on the MODBUS protocol, the address of each parameter, in the king view on the link can do, and I hope to adopt.
ABB converter supports MODBUS protocol, can be directly connected to the ModbusRTU in your choice of Kingview, device configuration, set up converter address directly in Kingview read the corresponding parameters can be
1, requires two communications. The PLC and the Kingview use a communication port individually, and the PLC and the inverter use a communication port alone. 2, Kingview and PLC communication time, Kingview is the master station, PLC is from the station; and PLC and converter communication, PLC is the master station, frequency converter is from the station. 3, frequency converter control, do not use communication, use digital point output and analog output. 4, PLC and inverter as the slave station using Kingview configuration; Wang put the data to the PLC, let PLC run the program, go to the PLC of the configuration parameters of the inverter control read out, and then sent directly from the Kingview converter.