Question:

Does the fire alarm host clearly specify how many points to take?

Does the fire alarm host clearly specify how many points to take?

Answer:

Yes, the specification provides that each circuit does not exceed 200 points, and the linkage point is not more than 100 points, each alarm host does not exceed 3200 points, and the linkage point is not more than 1600 points
The total number of devices and addresses should not exceed 3200, in which the total number of devices per bus loop is connectedShould not exceed 200, and should leave less than 10% of the rated capacity margin; any fire linkage controller
Fire detector, manual fire alarm button and module connected by any fire alarm controller