How does the MITSUBISHI PLC display the value of the pressure sensors and temperature sensors? Seek expert

How does the MITSUBISHI PLC display the value of the pressure sensors and temperature sensors? Seek expert

Answer:

AD module with analog to digital conversion, and then read the amount of digital BFM stored in the data register, and then you can see in the data register
PLC is just some data, PLC is completed A/D conversion, how to display, to see what to display, and then add some conversion
The hardware used in the temperature sensor and the pressure sensor is different.The temperature sensor value has a proprietary and temperature module to read its value, so it is possible to add a temperature module directly,The pressure sensor outputs a voltage value, or a current value, to read its value, there must be a AD module to determine the voltage value into the pressure value you want.So to display the temperature and pressure values, you have to add a AD module and a temperature module.