How to install a lightning arrester

How to install a lightning arrester

Answer:

(4) the contact surface of the arrester shall be wiped clean, remove the oxide film and paint, and coat with an electric composite grease.(5) the arrester shall be installed vertically, the deviation of the sag shall not be greater than 2%, and the metal plate between the flanges shall be corrected when necessary. The center shall be in the same line, the nameplate shall be on the same side as easily observed, the pressure ring shall be installed horizontally, and finally the surface shall be smoothed and coated with putty.(6) tighten the insulator string so that it is fastened, and the tension in the same sequence should be balanced so as to avoid the additional tension of the arrester.
(1) before the fixed arrester base, and then from the bottom up by each unit arrester installation group (section).(2) the arrester has been tested and qualified before leaving the factory. The site installation shall be assembled in strict accordance with the manufacturer's numbers, and shall not be interchanged so as to avoid changing the characteristics.(3) the valve type lightning arrester with series connection and parallel connection should be selected when installing, so that the nonlinear coefficients between the in-phase units are close to each other, and the difference should be no more than 0.04.
The discharge counter shall be well sealed, reliable in operation and consistent in the position of the three phase installation, so that it is easy to observe. Ground reliable, counter indicating zero recovery.(8) the exhaust passage of the Zinc Oxide arrester shall be unobstructed, and the exhaust gas shall be avoided during installation. It will cause interphase short circuit or ground flashover, and shall not spray other equipment.

Share to: