Load center wiring help???? Electrician advice please???

This question concerns the ground wires (bonding?) I am wiring a new workshop about 200 yds from my house. I plan to have the electric company drop a new line to a new meter for the building. I installed a homeline 200 amp, 30 slot load center and a cutler hammer top feed meter box. I ran 3awg wire for the weatherhead and main/neutral lug(s). My question is where does the #4 bare copper wires hook to? I have one tied into the rebar in the foundation and one hooked to a ground rod.1) In the meter box there is a smaller lug beside the neutral. Is this for a ground?2) In the load center I had to add a ground bar. There are neutral bars on each side of where the breakers go. There is a larger neutral lug on one neutral bar and another beside the incoming neutral lug.I‘m confused as to where these bare copper #4 wires go??? Please help, Thank you

Answer:

IN MAIN SERVICE PANELS GROUNDS AND NEUTRALS ALL GO TOGETHER. IN CALIFORNIA WE ARE REQUIRED TO GROUND TO YOUR PIECE OF REBAR 1( UFER GROUND)2 (GAS METTER OR GAS PIPE) AND 3 (WATER LINE OR WATER METER)OR SUPLEMENT WITH GROUND ROD. BUT ALL NEUTRALS AND GROUNDS GO ON THE SAME SET OF LUGS AND GROUND BAR. IF YOU ADDED A GROUND BAR THEN INSTALL THE LONG GREEN SCREW IN THE NEUTRAL BUS BAR SO THAT THE BOX IS ALL BONDED