Safety distance of explosion proof lamp and fire sprinkler in safe place

Safety distance of explosion proof lamp and fire sprinkler in safe place

Answer:

I. explanations on the design manual of sprinkler systems,Standard nozzles and obstructions:1) horizontal obstructions:The nozzle from the conventional splash plate lamps, air supply and exhaust air plane distance not less than 0.3m.
I. explanations on the design manual of sprinkler systems,Standard nozzles and obstructions:1) horizontal obstructions:The nozzle from the conventional splash plate lamps, air supply and exhaust air plane distance not less than 0.3m.Two. Explanation on the Handbook of rapid design for water supply and drainage engineering,The P317 twenty-third diagram indicates the minimum distance from the bottom of the edge of the beam or roof. In case of a high power bulb or an air outlet, the nozzle shall not be smaller than 0.80m.
Two. Explanation on the Handbook of rapid design for water supply and drainage engineering,The P317 twenty-third diagram indicates the minimum distance from the bottom of the edge of the beam or roof. In case of a high power bulb or an air outlet, the nozzle shall not be smaller than 0.80m.