It is expected that the power of the load equipment (computing server + ancillary equipment) is about 9KW, working for two hours in the event of power failure
How much battery is used?
How many pieces are right?
What is the reason for the calculation?
Recommended cost-effective one: Mountain ARRAY-MP-15KVA, +20 12V100AH maintenance-free battery, A20 cabinet, can meet the power at 9KW, power delay work for two hours. And the load is about 70%, the UPS run the best.
Product power: 12KW (kW)
Voltage input and output: single in single out
External battery voltage: 240V (DC) single block number: 20 blocks
Weight: 5 kg (kg)
Size: 436 * 775 * 443 MM
Application environment: small room
Simple calculation: (100 * 20 * 12 * 0.8) /9000=2.13H (hours)
Recommended cost-effective one: Mountain ARRAY-MP-15KVA, +20 12V100AH maintenance-free battery, A20 cabinet, can meet the power at 9KW, power delay work for two hours. And the load is about 70%, the UPS run the best.
Product power: 12KW (kW)
Voltage input and output: single in single out
External battery voltage: 240V (DC) single block number: 20 blocks
Weight: 5 kg (kg)
Size: 436 * 775 * 443 MM
Application environment: small room
Simple calculation: (100 * 20 * 12 * 0.8) /9000=2.13H (hours)
Recommended cost-effective one: Mountain ARRAY-MP-15KVA, +20 12V100AH maintenance-free battery, A20 cabinet, can meet the power at 9KW, power delay work for two hours. And the load is about 70%, the UPS run the best.
Product power: 12KW (kW)
Voltage input and output: single in single out
External battery voltage: 240V (DC) single block number: 20 blocks
Weight: 5 kg (kg)
Size: 436 * 775 * 443 MM
Application environment: small room
Simple calculation: (100 * 20 * 12 * 0.8) /9000=2.13H (hours)