Home > categories > Electrical Equipment & Supplies > Uninterrupted Power Supply (UPS) > Can maintain power close to 320W of the server running more than 8 hours of UPS power supply
Question:

Can maintain power close to 320W of the server running more than 8 hours of UPS power supply

The server power supply rated power is 400W maximum power 500W actual computer hardware power 270W over time plus 1 2 hard drive so count 300W in addition to a fiber optic transceiver less than 320W monitor with no power outage directly after the server in the company we Self-running site to prevent accidental power outage which can be maintained for 8 hours the server is running is best for 12 hours of the UPS brand does not need to be too good often a power outage occasionally can not be used enough points to add -

Answer:

In fact, the brothers say that you are a low-power low-power UPS charging capacity is simply not a good example APC SU series of machines 48V to the UPS with 8 hours of configuration results 1 hour are not up to the individual suggest that you actually come With 3K should be able to suggest your brand Hills because the mountain is a group of eight should be full charge
You 320 or about the power or use 1KVA of the UPS, but also with the best use of the battery line it, much more than the backup type of money,
500 + 300 +320 = 1120W can use 2KVAS UPS power supply, external 12 12V100AH battery (can be delayed more than 8 hours), external 18 12V100AH battery (can delay 12 hours) need to q me