Question:

Haier air conditioning compressor does not start

Haier 3P launched a few minutes to stop the compressor machine normal operation of the fan compressor hot water cooling compressor for several minutes and can start the compressor does not operate directly on the compressor test Chuang-tzu black and the other two different lines () this is the reason.

Answer:

Compressor hot, water cooling for a few minutes, the compressor can start, which is obviously the compressor temperature is too high, the protection stopped, and the cooling of the engine is not good, must be installed in the ventilation zone
Compressor overload, built-in overload protection action stop. After a few minutes, the temperature is down, the overload protection is reset and restarted. In this case, low voltage protection should occur.
The compressor start capacitor after the bad or insufficient capacity, will cause the compressor working in high temperature, overheating protection power, no refrigeration, usually after the shutdown time and short time work; if it is started can not be started, it is completely burned off the road starting capacitor, capacitor can completely replace! By the way, check again if the compressor power is connected properly!