Question:

How do I select a transformer connection group?

How do I select a transformer connection group?

Answer:

Both transformers are center-point direct-to-ground transformers. Dyn11 wiring group of the transformer because of its high-voltage winding is triangular wiring, so when the user produces three and three times the harmonic, can be formed in the triangular winding circulation, resulting in magnetic flux to eliminate this harmonic pollution for the grid. The Yyn0 transformer because there is no triangular winding, without this function. If only an independent power supply of small capacity transformer, you can use Yyn0 transformer, such a transformer everywhere, good production. If there is a transformer that may be supplied in parallel with other transformers, or as a backup power source for other power supplies, the same wiring group as other transformers should be selected. If it is recommended for large-capacity industrial transformers Dyn11 transformers are recommended to reduce the contamination of the grid by three or three times the number of harmonics.
Connection group can not be arbitrarily selected, depending on the primary transformer connection group. If the higher-level transformer for the star angle, the next level on the election star angle