Please tell me how to calculate the transformer in the lighting circuit of elevator shaft in building electrical design
The previous elevator hoistway lighting required the 36V safety voltage, and you can see how many power lamps are required for the hoistway, and select the transformer
Because of the brightness of the 36V safety voltage lamp brightness in the overhaul work is not enough, so now the well lighting design should not be 36V, and replaced by 220V, and only need to add a leakage protector on it.
Pe=19.5KW, installed capacityKx=1 coefficient of demandPjs=KxPe=19.5KW, calculated loadCOS, phi, =0.85, power factorIjs=KxPe/3/220/cos phi (Ijs calculates current, voltage, 380V/220V, three-phase)=1*19.5*1000/3/220/0.85=34.76A