I try to open my control panel or documents and I get a message saying windows explorer is not working and is restarting, it will just disappear after I close those windows and does nothing after that. I also keep getting a message DEP is not working as well, if I try to trouble shoot it, it will not let me. Help me please!!!!!!
Lube the chain after you have ridden.
Sorry, PVC is not allowed. Black pipe or CSST is normally used. The only plastic like pipe I know of, polymide and polyethylene, is restricted to outdoor or buried use. Keep in mind that there is a thing called the Authority Having Jurisdiction that can make a final determination. This would be the inspector. He has said it is not ok so the code would support him. NFPA 58 is the code book for gas piping although a state may or may not adopt it, or as it seems to be the case in California, may exceed what it says. Your inspector would know this and can provide you the code. Let me look up the code. Here it is 6.19 LP-Gas Systems in Buildings 6.19.2 Additional Requirements 6.19.2.4 Piping shall comply with Section 5.9 and shall have a pressure rating of 250 psig (1.7 MPag). 5.9 Piping (Including Hose), Fittings, and Valves 5.9.3 Pipe and Tubing 5.9.3.1 Pipe shall be wrought iron or steel (black or galvanized), brass, copper, polyamide, or polyethlene. Keep in mind that not all these pipes are for indoor use. ie: Polyamide and Polyethlene: 6.9.4.1 Polyethylene and polyamide pipe, tubing, and fittings shall be installed outdoors and underground only. PVC is not allowed. Since the inspector also says no you need to have the system re-plumbed.