Question:

What problems should be paid attention to when using the glass rotor flowmeter?

What problems should be paid attention to when using the glass rotor flowmeter?

Answer:

In order to avoid the deformation caused by the flowmeter due to pipe, flange and flange coaxial process pipeline must flow and parallel to each other, to support the pipeline to avoid vibration and reduce flowmeter axial load, control valve in the measurement system should be installed in the downstream of the flowmeter:
If the medium contains ferromagnetic material, a magnetic filter shall be installed; if the medium contains solid impurities, the filter shall be considered between the valve and the straight pipe;
In order to make the rotor flow meter work normally and achieve a certain measuring accuracy, the following points should be paid attention to when installing the flow meter:1. The rotor flowmeter must be mounted vertically on a non vibrating pipe. The fluid flows through the flow meter from bottom to top, and the verticality is better than 2 degrees. The horizontal angle is better than 2 degrees at the horizontal installation. (now there is a horizontal mounted rotor flowmeter)2, in order to facilitate the maintenance and replacement of flow meters and cleaning of measuring pipes, the metal pipe float meters installed on the process pipelines shall be equipped with bypass and bypass valves;3, the entrance of the rotor flowmeter should have 5 times the length of straight pipe above the pipe diameter, and the outlet should have 250mm straight pipe section;