How does the vertical template at the suspension stand?
Specifically, you can refer to the template specification above a detailed description of the roof template can also refer to this specification. Rebar acceptance is mainly to check the type of steel, diameter, anchor, lap, the number, location, arrangement, etc., steel acceptance can refer to the Atlas 03G101-1
Outside the wall perpendicular to the deviation, the roof template acceptance to be stretched to see flatness, template patchwork, template support and template is clean.
The vertical degree of the wall is less than 5m vertical height of the allowable deviation is <= 6mm, when the wall height is greater than 5m vertical tolerance is allowed to <= 8mm