Orifice plate flowmeter shall be equipped with condenser when measuring medium

Orifice plate flowmeter shall be equipped with condenser when measuring medium

Answer:

Standard orifice meters must be fitted with condensing containers when measuring steam, because the steam is divided into two types, one is saturated steam and the other is superheated steam. The temperature of saturated steam is generally between 150 and 300 degrees Celsius, and the temperature of superheated steam can reach 650 centigrade. Therefore, by condensing the container, the steam is condensed into water, and then connected to the differential pressure transmitter through the pressure taking pipeline, so as to avoid the direct contact with the differential pressure transmitter of the steam, thereby causing the temperature to be too high and damaging the differential pressure transmitter.
Generally need to be equipped with condensation tank, the general condenser tank at the top of the pipeline, and the two condensate tank at the same height
The condenser, which is also called the balancing pot, needs two:Condense the steam into waterTwo. Maintain the positive and negative pressure level balance of the differential pressure transmitter
Shenyang Shentuo automatic control equipment Co., Ltd. to remind you install condenser in standard orifice flow meter, two pressure condensing container to the same height and surface or cause two condensing vessel not as high error.