I have 200 13w lights and two computers, I use the 63A leakage switch, each time playing with a few hours and tripped, so repeated, would like to ask how to deal with? Thank you
Your total current is less than 15A, you can exclude is not overload and trip, must be occasionally leakage caused by the total leakage switch protection action, you need to first remove the lighting switch circuit is leaking (the method can be removed from the lamp to watch the lighting circuit Whether there is insulation less than 0.5 megohm), the general lighting leakage is less likely, the above exclusion should be caused by computer leakage, the need to repair the computer repair shop for processing.
The problem is simple. Leakage circuit breakers should be considered to be overloaded. If not installed on the basis of the increase in electrical equipment, should consider the aging of the switch damage, it is recommended to replace.
63A, after a few hours trip, should not be overcurrent.
If the lights and the computer has a switch, then only sub-section, and gradually narrow the scope.
Or changed to two: the lights do not have leakage protection circuit breakers, computers and sockets through the leakage protector.
1, not short-circuit problem (because of short circuit in any case, do not rule out the short-circuit point, the time interval can not work long after closing, continue to smoke, and instantly from short circuit into open circuit).
?????? 2, not load can not afford (because the leakage switch, leakage switch only for leakage when the action, no overload action function).
?????? 3, the biggest possible reason is because the kitchen is relatively humid, in the lamp connector, socket connector, control switch joints, leakage switch joints and other moisture, moisture is too large, resulting in leakage current, more than leakage switch action current (generally 30 mA ) And action, sunny weather may be better, rainy weather may intensify.