What are the technical parameters of the transformer?
Transformers in the provisions of the use of the environment and operating conditions, the main technical data are generally marked on the transformer nameplate. Mainly include: rated capacity, rated voltage and its tap, rated frequency, winding connection group and rated performance data (impedance voltage, no load current, no load loss and load loss) and total weight.
A, rated capacity (kVA): rated voltage. Rated current under continuous operation, can deliver capacity.
B, rated voltage (kV): the transformer can withstand long hours of operation can withstand the voltage to meet the needs of the grid voltage changes, the transformer has a high voltage side tap, by adjusting the number of high voltage winding to adjust the low voltage side of the output voltage.
C, rated current (A): transformer in the rated capacity, allowing long-term through the current.
D, no load loss (kW): when the rated frequency of the rated voltage applied to the end of a winding, the other winding open when the active power. And the core silicon steel sheet performance and manufacturing process, and the applied voltage.
E, no-load current (%): When the transformer in the rated voltage under the secondary side of the load, the current through a winding, generally expressed as a percentage of the rated current.
F, load loss (kW): the transformer secondary winding short circuit, in a winding rated tap position into the rated current, then the power consumption of the transformer.
G, the impedance voltage (%): the secondary winding of the transformer short circuit, in a winding slowly increase the voltage, when the secondary winding short-circuit current equal to the rated value, then the voltage applied once the general. As a percentage.
H, the number of phases and frequency: three-phase beginning to S said, single-phase start with D said. China's national standard frequency f is 50Hz. Foreign countries have 60Hz (such as the United States).
I, temperature rise and cooling: transformer winding or the upper oil temperature and the temperature difference between the ambient temperature of the transformer, known as the winding or the upper oil temperature rise. Oil-immersed transformer winding temperature rise limit of 65K, oil surface temperature rise 55K. There are a variety of cooling methods: oil from the cold, forced air-cooled, water-cooled, tube, chip and so on.
J, Insulation level: Insulation class standard. Insulation level of the method for the following example: high voltage rated voltage of 35kV level, low voltage rated voltage of 10kV level transformer insulation level expressed as LI200AC85 / LI75AC35, which LI200 said the transformer high voltage lightning impulse withstand voltage of 200kV, power frequency withstand voltage For the 85kV, low voltage lightning impulse withstand voltage of 75kV, power frequency withstand voltage of 35kV. Oaks High Technology Co., Ltd. The current oil-immersed transformer product insulation level LI75AC35, said the transformer high voltage lightning impulse withstand voltage of 75kV, power frequency Withstand voltage of 35kV, because the low pressure is 400V, can not be considered.
K, the connection group label: According to the transformer one. Secondary winding phase relationship, the transformer winding connected into a variety of different combinations, known as the winding group. In order to distinguish between different groups, often using the clock representation, that is, the high voltage side of the voltage phase of the clock as a long needle, fixed on 12, low voltage side of the phase voltage as the clock short needle, (A) is a (triangular) joint, and the secondary winding is a (star) junction with a center point, and the group number is (11).