Cable 4x185 + 1x95 need a large trunking

Cable 4x185 + 1x95 need a large trunking

Answer:

Cable laying is a bend radius, under normal circumstances the application of 400 * 200 bridge.
The total cross-sectional area of wires, cables, cables, cables, cables, cables shall not exceed 20% of the cross-sectional area of the trunking. Cable cross section of 4x185 + 1x95: 2875mm2 (YJV type cable). Calculate the truncated area of the trunking: 2875 / 0.2 = mm2. Select the trunking specifications: 200x100 (mm) mm2 & gt; mm2; qualified. Results: cable 4x185 + 1x95; its laying the smallest trough specifications: 200x100 (mm).
. according to the national standard GB / T.1-2008 method of calculation, YJV-4X185 +1X95 nominal diameter of not less than 53.7mm, usually between 54mm ~ 57mm. . the cable has power cables, control cables, compensation cables, shielded cables, high temperature cables, computer cables, signal cables, coaxial cables, fire cables, marine cables, mining cables, aluminum cables and so on. They are composed of single or multi-strand wire and insulation layer, used to connect the circuit, electrical appliances and so on. . outside diameter wàijìng [outsidediameter; externaldiameter] including the thickness of the pipe or container, including the outer diameter.
Reference outside diameter is 56.8mm you look at the wiring slot it