Can the water from the fire pump enter the roof fire tank? Why?

Can the water from the fire pump enter the roof fire tank? Why?

Answer:

Fire water pump water can not enter the roof, fire water tanks, "construction regulations" and "high regulations" clearly defined. The roof fire water tank acts as a temporary fire fighting water for 10 minutes, and the water in the fire pump is supplied directly to the indoor hydrant or sprinkler system. Roof water tank fire water can only be provided by the living pump.
Here is the concept of "fire water tank", if the roof has fire water tank, fire pump should be able to roof fire water tank water supply, as long as there is sufficient pressure on the line. However, if the roof water tank is only a living water tank, the fire pump is not started, this is the two pipelines.
This should be divided into two cases, the key depends on the use of your water tank!If you fire water tank roof is a constant pressure water tank fire control system, the requirements must be set on the water tank outlet check valve, which can only flow from the tank outflow, then pump the water can not enter the roof fire water tank.If the roof fire water tank acts as a water transfer tank and uses it to transport water to a higher building, the fire pump water can enter the water tank