Four wire pressure sensor signal positive and negative how to connect?

Four wire pressure sensor signal positive and negative how to connect?

Answer:

It is composed of four bridge arm resistance sensor circuit, it can output differential voltage signal and usually very weak, to be amplified by the amplifying circuit into a voltage signal is larger, or with a special circuit (signal conditioning) into 4~20mA current output.It is impossible to output 4~20mA directly, nor is the resistance.XTR105, XTR110, XTR112, XTR114 and other models are commonly used signal conditioners, you can achieve two-wire 4~20mA output.
The negative signal acts as the common end of the 4--20mA signal, that is, the reference zero potential.
A voltage signal is produced between the positive signal and the negative signal, and a current signal of 4 to 20mA can be obtained by proper resistance.