What are the requirements of the cable type temperature setting detector?
The insulation resistance of the detector shall be checked every six months to one year after the installation of the detector, and the result shall be up to the standard. Should be replaced promptly when found out of order.
5. when the electrical equipment detector directly installed in the above 36V when the alarm controller shell should be grounded.After the 6. detector is installed, no heating test is necessary, and the analog switch in the junction box can be used for testing.
1. installation should be used when the fixed fixture flame retardant plastics, interval should be 0.5m.2., the installation should prevent the detector from big knot, serious twist and strong bending, and its bending radius should be greater than 20cm.3. during the installation process, the outer sheath of the detector shall be protected, and the damaged material shall be coated with the same material at the same time.When the 4. detector is connected with the junction box and terminal box, the connection shall be reliable.
After the detector is shorted, the short joint should be removed and the detector with the same specification can be repaired. The detector can be continued after use.