Home > categories > Energy Products > Electricity Generation > Withstand voltage test, power equipment insulation unqualified reasons?
Question:

Withstand voltage test, power equipment insulation unqualified reasons?

Withstand voltage test, power equipment insulation unqualified reasons?

Answer:

Without proper consideration of the atmospheric conditions that affect the insulation characteristics. Because of the pressure, temperature and humidity have a certain impact on the spark discharge voltage and breakdown voltage, without considering these factors may lead to equipment failure.
Test methods and voltage measurement methods are not correct. For example, when the transformer is tested, the non - Test winding is not connected to the ground, and the non - tested winding may be discharged to the ground. For example, the test of large capacity test, the voltage is still on the low side of the measurement, due to the capacitive effect, the actual increase in the voltage on the test sample over the test voltage, resulting in the breakdown of the subject matter, misjudgment is not qualified.
Voltage test, power equipment insulation failure may be due to: insulation deterioration. Such as transformer oil into the water, solid insulation moisture, insulation aging, etc., will lead to decreased insulation performance, in the pressure test may not be qualified.

Share to: