Question:

Help on double pipe parallel heat exchanger?

3.A double pipe parallel flow HE is used to heat cold tap water with hot water. Hot water (cp=4.25 kj/kg C) enters the tube at 85 C at a rate of 1.4 kg/s and leaves at 50C. The HE is not well insulated and it is estimated that 3% of the heat given up by the hot fluid is lost from the HE. IF the OHTC and surface area of the HE are 1150 W/m2C and 4 m2 respectively, determine the rate of Heat transfer to the cold water and the LMTD

Answer:

pipe heat exchanger[/url] on the net. a simple googling will help you hope it helps
they are an financial decision for small exchangers that could basically require some common tubes. they are additionally a competent decision for smaller severe rigidity purposes. the alternative is often one according to economics. there is not any rule that determines the call technique.
Heat Transfer to the Cold Water: Qc = Qh*(1 - 0.03) where: Qh = mh*Cph*dTh = 1.4*4.25*(85-50) = 208.25 kW Qc = 208.25*0.97 = 202.0025 kW LMTD LMTD = Qc/(U*SA) = 202.0025/(1.150*4) = 43.9 C